Upgrading my thermostat. Have a new Honeywell wifi thermostat. My old thermostat only had two wires. Hooked to R and W on my furnace panel. My new thermostat says I need a C wire 24v common. My system is HEAT only and I don't need to control the fan separately. There is a C terminal on the furnace panel. I am wondering if I need to run a separate wire for the c wire and have all 3 wires hooked up on the new thermostat. Or can I switch the R wire over to the C on the panel.

Thanks


Sent from my iPhone using Tapatalk -
 

jeffg463

Active VIP Member
Joined
Dec 1, 2008
Messages
199
Reaction score
23
Location
Edmonton
what model of honeywell is it Maxwell? If it's wifi does it have a wired sending unit to be mounted at the furnace and then a wireless 'stat?
 

Twacked

Active member
Joined
Mar 21, 2012
Messages
39
Reaction score
34
Location
Shuswap
You have to bring a common wire up to the stat to "power" the stat. Will not work without. While ur at it you might as well pull up more control wires so you can control your fan from the stat as well. Do u plan on installing a/c? If u do you'll need some for that as well. Put in 18/6 you should be covered.
 
Last edited:

maxwell

Active VIP Member
Joined
Apr 25, 2007
Messages
19,927
Reaction score
42,177
Location
Sherwood Park, Alberta, Canada
what model of honeywell is it Maxwell? If it's wifi does it have a wired sending unit to be mounted at the furnace and then a wireless 'stat?

Nope by wifi I mean I can control it anywhere from my phone. Since IM hardly ever home.

It's a RTH9580WF


Sent from my iPhone using Tapatalk -
 

maxwell

Active VIP Member
Joined
Apr 25, 2007
Messages
19,927
Reaction score
42,177
Location
Sherwood Park, Alberta, Canada
You have to bring a common wire up to the stat to "power" the stat. Will not work without. While ur at it you might as well pull up more control wires so you can control your fan from the stat as well. Do u plan on installing a/c? If u do you'll need some for that as well. Put in 18/6 you should be covered.

That's a good idea. I can use the old wire to pull the new stuff through the wall. Is it called 18/6 thermostat wire just at Home Depot or? I don't have plans for ac but you never know!


Sent from my iPhone using Tapatalk -
 

Twacked

Active member
Joined
Mar 21, 2012
Messages
39
Reaction score
34
Location
Shuswap
The wire you want is called LVT. Chances are the existing 2 wire is stapled to the stud and you will not be able to pull with it. The LVT you want is 18 gauge/ 6 conductor. Hook up the g terminal as well and you'll be able to control the fan from the stat. And c,r,and w.
 
Last edited:

hbar218

Active VIP Member
Joined
Sep 10, 2007
Messages
707
Reaction score
1,343
Location
Edmonton AB
if it has batteries in the stat you don't need a c wire, but if batteries die you will not have heat
 

Twacked

Active member
Joined
Mar 21, 2012
Messages
39
Reaction score
34
Location
Shuswap
For the perticular stat you have, you need the common wire for the stat to function I've been installing these since they came out. If you can't get a common wire ran there is another honeywell stat that only requires 2 wires but it is way more expensive and the wifi gateway is a seperate component.
 

maxwell

Active VIP Member
Joined
Apr 25, 2007
Messages
19,927
Reaction score
42,177
Location
Sherwood Park, Alberta, Canada
if it has batteries in the stat you don't need a c wire, but if batteries die you will not have heat

Read a lot of negative reviews about it....maybe it's better now. got this one working and very happy with it